minimum motor sealing requirement for coal fired power plants

minimum motor sealing requirement for coal fired power plants

minimum motor sealing requirement for coal fired power plants

(OP)
The folks on the power plant engineering forum suggested I repost here.

We provide some motorized equipment for use in coal fired power plants.  Even on indoor installations Pulverized coal dust is everywhere, even in the real clean ones. The question comes up as to whether WP2 with filters or even TEFC sealing is required to protect the windings, etc. Quite a price difference on a 1000 HP motor.

I'm interested in real life experiences.

thanks


Dan T

RE: minimum motor sealing requirement for coal fired power plants

In my other life, all draft fans (induced draft and forced-draft) were of the TEFC types. Its not coal dust alone that you have to deal with, but some very fine ash floating around!

RE: minimum motor sealing requirement for coal fired power plants

In closed or confined area where coal dust may be in suspension for a long time, according to NFPA 70 [NEC]
the area is classified as Class II division 1. Coal dust is Group F. See NEC Art.502
Motors in Class II-Division 1 locations must be explicitly rated (dust-ignitionproof) for those areas
or be totally enclosed pipe ventilated (TEPV) with approved maximum surface temperatures.
The autoignition temperature of the coal depends on volatile contents of the coal. At high volatile contents, the ignition temperature of a coal dust layer approaches a limiting temperature as low as 160oC (320oF).
The wiring has to be as per art.502 and sealing shall be done where required.
See also:
http://www.brookcrompton.com/pdf-files/2203e_hazcat_v1.pdf
http://www.am.pepperl-fuchs.com/pdf/documents/eg06_p007-96_engineer_guide.pdf
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources