Sorry for this off-the wall- question, but need to know. I am a structural engineer in building design. However, I am asked from time to time to help architects design supports for counter tops. Not hardly main building structure, but asked anyway and I try to help.

I can't find a document or reference for what would be a good point load to use for counters. Don't find in code, and Google hasn't helped so far. I would expect that as much as 200 lb would be normal in case someone sits on it.

Anybody know what's typically done?

Thanks!

RE: Design loads for counter tops

I've never been able to find good design criteria for furnishings which is probably why they break on occasion.  I usually lean on the ADA 250lbs design requirement for shower seats and benchs when asked and would probably use the same for a countertop.

RE: Design loads for counter tops

I've designed many countertops, including computer work stations and restroom counters.  I use 300 pounds concentrated load plus dead load and design each support to carry that, assuming there is no load transfer to other supports.  That will take care of pretty much anything, including the maintenance guy standing on the counter to change a light bulb.

RE: Design loads for counter tops

(OP)
Thanks to all for your responses.

I wound up using DL plus 3 - 200 lb point loads at equal spacing. The counter is about 16' long. I sized a tube to limit deflection to protect surface - has lots of reserve strength capacity.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources