(OP)
I have a ESP pumps skid, the configuration is 400VAC incoming - VFD - step up transformer 0.4/3.6KV - ESP pumps (280kW), this skid is powered by 400vac genset, my question is the minimum capacity of genset?  

RE: Genset capacity slection

Since you have a soft start via VFD, 400 KVA should do it.

Muthu
www.edison.co.in

RE: Genset capacity slection

(OP)
If it is 400V GENSET to 400V motor, it is OK. But it is 3.6KV ESP pump, 400V genset - step up transformer 3.6KV - ESP pumps,  the MV pumps starting shall be considered in this case.  

RE: Genset capacity slection

Your 20kW plus losses may end up closer to 325kW.
200% is often recommended for VFD drives due to AVR stability issues.
Try about 600kW for the genset.

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources