Genset capacity slection
(OP)
I have a ESP pumps skid, the configuration is 400VAC incoming - VFD - step up transformer 0.4/3.6KV - ESP pumps (280kW), this skid is powered by 400vac genset, my question is the minimum capacity of genset?





RE: Genset capacity slection
Muthu
www.edison.co.in
RE: Genset capacity slection
RE: Genset capacity slection
200% is often recommended for VFD drives due to AVR stability issues.
Try about 600kW for the genset.
Bill
--------------------