VFD Harmonics
VFD Harmonics
(OP)
I'm designing a facility with a 600V, 1000A electrical system and the majority of the loads are 6-pulse VFD's with input reactors. The utility has informed us that we do not have to meet the IEEE 519 standards for harmonics.
Would adding harmonic filters to the VFD's still be worth the expense in this case? What possible harmonic-related problems could occur within the facility if they're not installed? (The primary loads are large VFD's, small motors and building loads, UPS for PLC control system.)
Would adding harmonic filters to the VFD's still be worth the expense in this case? What possible harmonic-related problems could occur within the facility if they're not installed? (The primary loads are large VFD's, small motors and building loads, UPS for PLC control system.)





RE: VFD Harmonics
If your larger VFD are having 12-pulse input rectfifiers the harmonics from the 6-pulse units may cause imbalance between bridges that are connected in parallel.
RE: VFD Harmonics
These questions need to be addressed for a quality answer, but for a quick and DIRTY answer. If your source is stiff (low impedance), then you are probably ok. If your source is soft, high impedance, then the voltage may get ugly. The VFD's probably won't care, but some lighting and control systems might not play well.
If you are just now in the design phase then I would definitely pursue a quality answer. You'll save yourself headaches in the future as the system grows.
Neil
RE: VFD Harmonics
Neil
RE: VFD Harmonics
There are two 250hp Schneider 6-Pulse VFD's. All other plant loads are less than 50kVA total, and mainly supplied by a 120/208V three phase transformer. Lighting is all fluorescent. The lighting transformer could be harmonic mitigating or k-rated if this helps. The main utility service transformer will be 750kVA, so I suspect the impedance is fairly low for the existing loads.
In the future, up to two additional 250hp VFD's will be installed to meet the process demands.
I suspect that harmonics would not be an issue until the new loads are added many years from now. Would it be alright to allow for space for harmonic filters to be installed in the future but not worry about them for now?
RE: VFD Harmonics
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: VFD Harmonics
You could even divide the load in thirds and buy a transformer with three secondaries, a wye, a delta, and a zigzag. These are intended for 18 pulse drives but if the loads all operate together, put one third of the kw on each secondary and you will have 18 pulse performance.
RE: VFD Harmonics
Line reactors will certainly help with the harmonics, likely reducing the current distortion from 100% plus levels to around 30% or so. The solution DickDV suggests would do even better, likely getting below 15% current distortion. Any other "off the shelf" product to reduce the harmonics further gets quite pricy. A single custom passive harmonic filter or a single active filter would likely be price competitive when looking at 1000hp of VFD to filter.
RE: VFD Harmonics
Neil
RE: VFD Harmonics
You indicate the utility company is advising your harmonic distortion will be too much: by how much and on what basis have they made this assumption?
It is quite feasible to introduce either active or passive harmonic filtration at a later date and as long as you have the space and ability to connect, it may be prudent to do it this way as the simple answer is that actual measurement will define the level of harmonic mitigation you need.
Once you know this, sometimes you will find that the level of harmonic canceling is minimal. 12 pulse configurations need to be rated for the full amps of the drive system whereas active filtering only need to be rated for the offending harmonic amps.