Toe nailing with lag bolts
Toe nailing with lag bolts
(OP)
Builder did nailed double seal plate to the wood girder beam. I have wind loading on walls. Found out that I do not have required capacity for the shear, need to use lag bolts, and wall already covered. Since the floor is elevated I can make required connection from the bottom (going through the triple 2X12 girder beam up to the the 2x6 double seal plate), but the way it can be done only installing 1/2" lag bolt on an angle, same principle as "toe nailing". Is it possible to use 1/2" bolt for toe nailing? Or may be there is better way to take care of shear?






RE: Toe nailing with lag bolts
RE: Toe nailing with lag bolts
RE: Toe nailing with lag bolts
RE: Toe nailing with lag bolts
RE: Toe nailing with lag bolts
I assume then that it is the shear in the inside ply face that is the problem.
That said, if you place Simpson A35's, or similar, flat along the sill plate, triple beam interface line at the proper spacing, they should be able to transfer the shear from the sill plate to the triple joist.
Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
RE: Toe nailing with lag bolts
Garth Dreger PE
AZ Phoenix area
RE: Toe nailing with lag bolts
BA
RE: Toe nailing with lag bolts
RE: Toe nailing with lag bolts
BA
RE: Toe nailing with lag bolts
Are you saying then that the floor diaphragm is not secured adequately to the girder beam?