How Many A325 Bolts to Spot Check
4

How Many A325 Bolts to Spot Check

How Many A325 Bolts to Spot Check

(OP)
Does anyone know the percentage of bolts to spot check on a structural steel building. Any tips will be greatly appreciated.  

RE: How Many A325 Bolts to Spot Check

I an sure it is somewhere in the standard. I use 10%
 

RE: How Many A325 Bolts to Spot Check

Do you mean on a site visit?

RE: How Many A325 Bolts to Spot Check

cap 4000...I use 10% of the connections, checking each bolt in that particular connection.  There are no standards for that, but it's consistent with other test and observation frequency in construction.

RE: How Many A325 Bolts to Spot Check

Type of framing will impact the estimate.  Braced frames have many more bolts than welded moment frames.   

http://www.FerrellEngineering.com

RE: How Many A325 Bolts to Spot Check

Were the bolts tested (preinstallation verification testing) on-site by the erector as per RCSC?

What type of connections are they; Slip critical, snug tight, pretensioned?

Is this an existing structure or are you checking the bolts during erection?

Check the recommendations of the RCSC for arbitration inspection. I believe you can get the RCSC on line.

Specification for Structural Joints Using ASTM A325 or A490 Bolts

It is like the Prego spaghetti sauce commercial - "It's in there."
 

Best regards - Al  

RE: How Many A325 Bolts to Spot Check

Sorry I miss understood the question.  Percentage of bolts to be field inspected.

Prior to installation, for pretensioned installation, a sample of not less than three assemblies of each type (diameter, length, grade, lot), shall be tested before installation.

During construction...
snug-tight connections - shall be visually inspected to verify that all plies are in firm contact.

pretensioned connections - RCSC requires "routine" observation of the installation method selected.

If it is determined after installation that proper pretensions have not be been obtained, additional procedures are given in the Arbitration section of RCSC.

Additional inspection guidelines can be provided within the contract documents.  

  

http://www.FerrellEngineering.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources