Touch / Step Voltage

Touch / Step Voltage

Touch / Step Voltage

(OP)
My general engineering knowledge says that touch potential should not increase 50Volts for AC system. But I am seeing that normally in grounding/ earthing calculations we get this voltage much higher that is tolerable and is around 367V/976 V (Touch/Step) (it is not constant and varies with the bar arrangements, Soil resistivity etc).

Can someone clarity?

Thanks in advance.

RE: Touch / Step Voltage

I don't think a touch or step potential of those magnitudes would be tolerable to someone actually experiencing it.   

David Castor
www.cvoes.com

RE: Touch / Step Voltage

Tolerable step- and touch- voltages in substations depend on fault duration and the resistivity of the surface layer.  See IEEE Std 80-2000.  What is the basis for you "general engineering knowledge"?

RE: Touch / Step Voltage

(OP)
My general engineering is from codes only. I think I must clearity more for my raised point.

For fault times greater than 600ms(Heart beat time) the affordable touch Potential should be around 50V. But for 0.5Second fault current I am getting the values stated in OP (367V) in ETAP calculations.

RE: Touch / Step Voltage

The following clarification may be appropriate:
•    Tolerable voltages of 367V and 976 V are within ranges for usual allowable step and touch potentials.
•    The grid arrangement will affect the current injected into the ground and the allowable voltages.
•    Check the applicable code for earthing (grounding) in substation. Most programs including the ETAP may be set to calculate the allowable voltages in accordance with the IEEE Std 80 or IEC/CENELEC or similar.
•    IEEE Std 80 provide an allowable step and touch potentials of ~164V for o.5 sec for 50 kg person neglecting the footage resistance and surface resistance (crushed rock). Those resistances provide larger allowable voltage comparable to the one calculated by ETAP program.
 

RE: Touch / Step Voltage

CORRECTION:

•    The grid arrangement will affect the current injected into the ground BUT NOT the allowable voltages.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources