Need equipment to manually switch 16 - 515 VDC circuits
I am looking for a solution to manually or automatically switch:
14ea 515 VDC circuits 140 amp
2ea 515 VDC circuits 44 amp
to a single combined output, switchable between two loads.
Any help or suggestions would be GREAT!
RE: Need equipment to manually switch 16 - 515 VDC circuits
Try Hubbell. Their line of former Euclid Crane controls might have something suitable.
Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.
PV? (Photovoltaic)
I have seen traction contactors being used sucessfully in such applications.
Gunnar Englund
www.gke.org
There were a couple of threads a few weeks ago regarding generator field contactors, which is a fairly severe DC switching application. A handful of contactor manufacturers cropped up: Hubbell, Telemechanique, ABB, GE and maybe one or two that I can't think of right now. Might be worth looking for those threads. wink
I would not switch under load. Yes this is for PV.
If you can GUARANTEE that you will not switch under load, then you can use just about anything. But it is a very difficult thing to guarantee. So, go for standard DC contactors. Safe or sorry - that's the question.
I recently did measureents on a 2500 kW PV plant. Panels were switched in groups and DC contactors were used.
Gunnar Englund
www.gke.org