Use Cedar Shake Roof as a continuous diaphragm?

Use Cedar Shake Roof as a continuous diaphragm?

Use Cedar Shake Roof as a continuous diaphragm?

(OP)
Hi guys.  Here's the problem:

I'm working on a large custom single family home on the east coast and it requires a full IBC lateral design.  The owner is looking to use a traditional cedar shake roof, which uses 1x4's across the rafters to support the shakes instead of using plywood/osb roof sheathing.  Normally, you would count on the roof sheathing as your diaphragm to transfer the lateral loads to the gable end shearwalls.  However, in this case, I don't know that I can call the roof a continuous diaphragm without the plywood.  Also, there are no published diaphragm values that I could find for a roof framed in this configuration.

Ideas?  

RE: Use Cedar Shake Roof as a continuous diaphragm?

If you look here:
http://www.cedarbureau.org/installation/roof_manual/page03.htm#
there is a design option for continuously sheathed roofs, and still considered "traditional" shake.  I'd say that this would be the best way to go for a full lateral design.

Here's the full manual:
http://www.cedarbureau.org/installation/roof-manual.htm

They also say they've tested the system using plywood sheathing but not OSB.

I hope that helps a bit...

RE: Use Cedar Shake Roof as a continuous diaphragm?

You could use the ceiling Gypsum Board for a diaphragm if your shear is low. See IBC table 2508.5.

Garth Dreger PE
AZ Phoenix area

RE: Use Cedar Shake Roof as a continuous diaphragm?

Check out the document ATC 7-1, Proceedings of a Workshop on Design of Horizontal Wood Diaphragms, Nov 19-20, 1979. It presents methods of determining capacities of the diaphragm you describe. It's the "Nail-Couple Method" and is very straight forward.

http://www.atcouncil.org/pdfs/atc7-1toc.pdf

I also have seen it described in the Western Woods Use Book chapter on designing for lateral forces.

RE: Use Cedar Shake Roof as a continuous diaphragm?

1. i think (?), suspect, the nail couple design methodology, although common years ago, is no longer accepted.
2. on the west coast, where the APA-EWS supervises most of the plywood / osb sheathing, APA-EWS will support he use of properly rated OSB as equivalent to properly rated plywood for lateral support.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources