No load amps with Powerflex 700

No load amps with Powerflex 700

No load amps with Powerflex 700

(OP)
I have a 60hp AC motor controlled by a ABB Powerflex 700 Vector control drive. I notice that the no load amperage is 21A. Is this normal? ie. Is the no load amperage with drive control usually higher than using a DOL starter? If yes, why?

 

RE: No load amps with Powerflex 700

That depends entirely on how the drive parameters are set up.  We really can't answer your question without knowing more about how the drive is configured.

Also, you either have an Allen-Bradley PowerFlex 700 or an ABB drive of some model.  Note that these are two different brands.

RE: No load amps with Powerflex 700

21 A without load is ok. As a rough estimate the No-load current should be < 1/3rd of the FLC.

RE: No load amps with Powerflex 700

The no load current looks ok. A 60hp motor would be about 70~75FLA, so 21A seems about right, assuming 460Vac.
As DickDV points out, if the settings on your PF700 are not correct or the vector algorithm is not tuned correctly, then you could get over-excitation and hence more current at no load.

RE: No load amps with Powerflex 700

(OP)
Correction: It is an Allen Bradley Powerflex 700 drive
The motor nameplate is as follows:
Reliance Electric Inverter Duty Motor
Frame: 364T
Hp: 60
RPM: 2475/2680
V: 460
Amps: 68.2/67.6
Hz: 83/93

The drive parameters:
Rated kW: 45
Rated V: 480
Rated Amos:77
Motor Type: Induction
Motor NP V: 460
Motor NP FLA: 68.2
Motor NP Hertz: 83
Motor NP RPM: 1750
Motor NP Power: 60
Motor NP Pwr Units: Horsepower
Motor Cntl Sel: FVC Vector

Any other info required?

 

RE: No load amps with Powerflex 700

For 68 Amps FLC, 21 amps is quite normal.

Thumbrule - No load current = 1/3rd rated current

Muthu
www.edison.co.in

RE: No load amps with Powerflex 700

it would appear to be a special motor winding at 83Hz but again, nothing too concerning about the no-load current. However, how did you establish that the DOL current was lower? (meaning, where did you get 83Hz as a base supply frequency other than from your VFD?)

RE: No load amps with Powerflex 700

Correction to my question just now: I didn't read your own question properly and had it in my head you had tried it DOL.

RE: No load amps with Powerflex 700

Could you describe what type of load you are driving? I would expect to see more than a 21amp no-load from a 4 pole motor at 1750 unless there is some type of stored mecahnical energy,  such as a flywheel, "helping the load" in the system.

RE: No load amps with Powerflex 700

electromike,

The vast majority of the no-load current is magnetising current, with a small in-phase current to meet the iron, copper and windage losses. Nothing you do to the shaft will modify the magnetising current because that is inherent in the design of the motor stator and rotor.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: No load amps with Powerflex 700

The important current is at full load. Then it should be rated current.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources