High Capacity Metal Deck Diaphragms
(OP)
Are there any tricks to bumping up the allowable psf in a non composite metal deck for diaphragm shear load transfer?
Has anyone ever used two layers metal deck, layed right over each other? Is there some special weld pattern or type of deck? I'm trying to use a 1.5 type B.
We have a project with relatively small area of the oveall roof diaphragm bordered by diaphragm openings (clerestories)I have a flexible, irregular diaphragm attached to a masonry shearwall in this location.
I would love to keep the same gauge deck everywhere althouh even with the heavier guages and tigher joist spacings I'm having problems falling under the allowables given in the metal deck supplier's design book.
Has anyone ever used two layers metal deck, layed right over each other? Is there some special weld pattern or type of deck? I'm trying to use a 1.5 type B.
We have a project with relatively small area of the oveall roof diaphragm bordered by diaphragm openings (clerestories)I have a flexible, irregular diaphragm attached to a masonry shearwall in this location.
I would love to keep the same gauge deck everywhere althouh even with the heavier guages and tigher joist spacings I'm having problems falling under the allowables given in the metal deck supplier's design book.






RE: High Capacity Metal Deck Diaphragms
I have used the products in the past for decks with up to 1200 plf of shear.
RE: High Capacity Metal Deck Diaphragms
Thanks.
RE: High Capacity Metal Deck Diaphragms
The attached file is from the ES report from Verco
For capcities, you will want to look at ICBO ES Report-ER2078
RE: High Capacity Metal Deck Diaphragms
http://www.sdi.org/manuals.htm
I assume you are aware that increasing the number of welds or intermediate fasteners will increase the allowable shear values. However, it is not clear whether the welds or the deck are controlling the design, so I am not sure how to quantify the capacity of two layers of deck. Just a thought; perhaps you could use two layers of deck with a 36/7 weld pattern and take double the value of a single layer with a 36/4 weld pattern.