(OP)
New here to the forum. I have a project to implement Zone Selective Interlock (ZSI) on a 480V bus (Y-connected) system using CH Digitrip RMS 520 LSIG. I will like to disable the "ground fault" function on the main breaker and some feeder breakers feeding the MCC and large motor downstream. We have experienced spurious ground trips in the past on this bus each time a piece of equipment is been put back in service. Has anyone have success doing this without any detrimental effect on the equipment? Any help is highly appreciated.

RE: CH DigiTrip RMS 520 ZSI

If you are in the US, there are NEC requirement for GF protection that you may have to comply with.

Generally, nuisance GF trips can be reduced by increasing the time delay.   

David Castor
www.cvoes.com

RE: CH DigiTrip RMS 520 ZSI

It's usually not possible to disable GF if the trip unit is equipped with it.

Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.

RE: CH DigiTrip RMS 520 ZSI

You may need to get rid of the ZIS so that each breaker's GF pick up and time delay can be set independently.

With ZSI on, the downstream breaker defaults to minimum TD or INST (no intentional time delay). This may be the cause of some of your nuisance trips. A device with a ground fault would not always coordinate with the downstream breakers without GF.

Also have someone experienced look at the coordination.

Rafiq Bulsara
http://www.srengineersct.com

RE: CH DigiTrip RMS 520 ZSI

When the ZSI input is activated it raises the time delay setting of the Main breaker GF protection.  If teh nput is ot present, the GF trips instantaeneously.  It may be that your downstream feeder breakers are a little slow in sending the ZSI to the Main breaker or the wiring may be defective.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources