Current densities in dry type VPI transformers

Current densities in dry type VPI transformers

Current densities in dry type VPI transformers

(OP)
I want to spec a 500 KVA, 6.6 KV/415 V, 50 Hz indoor dry type VPI (not cast resin) transformer. For a temperature rise of 60 deg C over an ambient of 40 deg C, what arr the current densities I should specify for the HV & LV windings ? Conductors for both windings will be enameled, fibre glass covered rectangular conductors. No foil windings.

Muthu
www.edison.co.in

RE: Current densities in dry type VPI transformers

Sounds like a special order? I would not specify current density on a small transformer such as this. Just maximum temperature rise.

Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.

RE: Current densities in dry type VPI transformers

(OP)
Thanks Alan. I want to spec the current densities to bring the bidders on the same platform.

Muthu
www.edison.co.in

RE: Current densities in dry type VPI transformers

Muthu,As per today's capitalisation rates, the following specific loadings are followed by manufacturers.
Conventional dry type- B=1.60-1.65T Current Density-HV 2.5 A/mm2 LV =2A/mm2. In case of cast resin it is limited to 1.6 -1.7 A/mm2. Your idea of asking for  maximum benchmark specific loadings so that  you can compare competitive bids esp with regard to  actual  net active part( Cu &CRGO)  weights is a clever idea which I had been propogating to customers,but in vain.

RE: Current densities in dry type VPI transformers

(OP)
Thanks prc. Since I am buying the trafo for own use, I am willing to pay the bucks for quality. My proposed specs are 1.5 T max, 2 A/mm2 for both HV & LV.

Since you're into manufacturing, what would be your rough estimate for a dry type, VPI treated trafo of 500 KVA, 6.6 KV/415 V, 50 Hz with the above specs ?

Muthu
www.edison.co.in

RE: Current densities in dry type VPI transformers

Why do you go for 1.5 T.You will unnecessarily incur cost with out value.Ask for prime CRGO from reputed origin( with stage inspection clause) and go for 1.6 /1.65 T .Specify that  you will physically check the specific loadings during manufacturing stage.Rough estimate 0.7 MINR

RE: Current densities in dry type VPI transformers

(OP)
This trafo will be fed by VFD and hence such low B and current density. Could you possibly send a quote to me ? I am looking for 500 KVA, dual voltage wye connected secondary 6.6-3.3 KV and 415 V delta primary, indoor, dry type VPI windings.

Muthu
www.edison.co.in

RE: Current densities in dry type VPI transformers

Why not evaluate losses if you want to get all bidders on the same basis?  Why do you care if one manufacturer has higher current density if the transformer meets temperature rise specs, except for higher losses which can be evaluated economically?
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources