I want to spec a 500 KVA, 6.6 KV/415 V, 50 Hz indoor dry type VPI (not cast resin) transformer. For a temperature rise of 60 deg C over an ambient of 40 deg C, what arr the current densities I should specify for the HV & LV windings ? Conductors for both windings will be enameled, fibre glass covered rectangular conductors. No foil windings.
Muthu
www.edison.co.in






RE: Current densities in dry type VPI transformers
Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.
RE: Current densities in dry type VPI transformers
Muthu
www.edison.co.in
RE: Current densities in dry type VPI transformers
Conventional dry type- B=1.60-1.65T Current Density-HV 2.5 A/mm2 LV =2A/mm2. In case of cast resin it is limited to 1.6 -1.7 A/mm2. Your idea of asking for maximum benchmark specific loadings so that you can compare competitive bids esp with regard to actual net active part( Cu &CRGO) weights is a clever idea which I had been propogating to customers,but in vain.