loss in a dist. system
suppose i have flow losses totaling 500gpm at about 80psi in a dist. system. if i reduce the pressure to say 50psi, what kind of reduction in flow losses would you expect? i would use flow through an orifice i suppose as a first start to approximate this but suggestions are welcome. thanks.
RE: loss in a dist. system
"........ since leakage rates are directly related to system pressure, lowering the pressure will reduce water loss from any existing leaks. For example if a portion of the distribution system has leaks totaling 500gpm with a pressure of 80psi, the leakage will be reduced to 105gpm (nearly an 80% reduction) by lowering the pressure to 50psi........"
i know the pressure drop varies with the square of the velocity but maybe i missed something here...
Q = 19.65 (d) (d) C (sq root h)
If you assume all of the pressure is headloss, then;
Square root of 80/square root of 50 = 1.25. So that would be a decrease in flow of 25% going from 80 psi to 50 psi.
I would prefer to state the proposed leakage reduction in a range of values rather than a specific number. The proposed leakage reduction is nothing more than an educated guess.
so... something's wrong with the statement? i.e. we would expect the flow to reduce the same percentage as the pressure.
C = orifice coefficient (0.6)
a = area of orifice sq ft
g = 32.2
h = head in feet
using the orifice equation, the result is approximately 21% less flow going from 80 to 50 psi. CH2M Hill was wrong - go figure...