Hi
I have come across Yaskawa J1000 family of inverters and am considering purchasing one to control a pump on a variable frequency.
I have read a few posts in this forum where the voltage used was slightly different to the rating of the inverted and this led to over excitation and tripping.
If the inverter is 3 phase 400 V and I plan to use 415 or 430 V (3kW 50 Hz)should this make a large difference to the operation of the pumps motor?
Justin
I have come across Yaskawa J1000 family of inverters and am considering purchasing one to control a pump on a variable frequency.
I have read a few posts in this forum where the voltage used was slightly different to the rating of the inverted and this led to over excitation and tripping.
If the inverter is 3 phase 400 V and I plan to use 415 or 430 V (3kW 50 Hz)should this make a large difference to the operation of the pumps motor?
Justin





RE: Yaskawa Drive
Not quite sure what you mean with the 400 and 415/430 volts? Do you have a 415/430 V motor and a 400 V mains voltage? If that is so, you will not be able to feed the motor with the correct voltage. But certainly no risk for overexcitation. Rather the opposite.
If you have a 415/430 V grid and the VFD is made for 400 V, you may also be OK, most inverters can easily work with elevated voltage. Some have a rather broad input voltage range.
Also, most motors can tolerate up to a +/-10 percent deviation from nominal U/f ratio.
Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
RE: Yaskawa Drive
When I posted the above I only had the brochure for the drive which stated 400V. I was a little worried that if I was installing on a site that the voltage may be 415 or 420, would this affect the operation of the drive and subsequently the pump motor.
I have since found the data sheet on line and can see that the rated power supply voltage is from 380V to 480V.
Thanks again
Justin