Are IEC Soft-Starters placed in the conventional switchboard/MCC, or is there special switchboard/MCC for soft starters?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: IEC Soft Starters
Can't imagine why IEC units would not be able to do the same.
Rafiq Bulsara
http://www.srengineersct.com
RE: IEC Soft Starters
RE: IEC Soft Starters
Rafiq Bulsara
http://www.srengineersct.com
RE: IEC Soft Starters
RE: IEC Soft Starters
Some factors to consider include: whether you can accept ventilation apertures on the board, whether forced draught cooling is acceptable or natural draught only, acceleration time of the load, presence of bypass contactor, etc.
Generally, yes the soft start cubicle will be larger. For a ballpark figure, double the size, but consider the comments above.
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: IEC Soft Starters
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: IEC Soft Starters