IEC Soft Starters

IEC Soft Starters

IEC Soft Starters

(OP)
Are IEC Soft-Starters placed in the conventional switchboard/MCC, or is there special switchboard/MCC for soft starters?

RE: IEC Soft Starters

Soft starters  and VFDs are routinely built in the 'conventional' MCCs along with conventional starters even, in the NEMA world.

Can't imagine why IEC units would not be able to do the same.

Rafiq Bulsara
http://www.srengineersct.com

RE: IEC Soft Starters

(OP)
What is the approximate relation between the dimensions of the conventional-starters and soft-starters. For example, if a 100HP conventional starter is 12"H X 8"W X 6"D, then what will be the approximate dimensions of equivalent 100HP soft-starter?

RE: IEC Soft Starters

(OP)
I will check catalogues, but for now I just want to get a general idea whether the soft starters have bigger dimensions than the conventional starters; or are the smaller in size than conventional starters?

 

RE: IEC Soft Starters

'It depends!'

Some factors to consider include: whether you can accept ventilation apertures on the board, whether forced draught cooling is acceptable or natural draught only, acceleration time of the load, presence of bypass contactor, etc.

Generally, yes the soft start cubicle will be larger. For a ballpark figure, double the size, but consider the comments above.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: IEC Soft Starters

Quote (timm333):

I just want to get a general idea whether the soft starters have bigger dimensions than the conventional starters; or are the smaller in size than conventional starters?
I think Scotty's answer is a good safe way to approach it, double the size in most cases. In any case, a soft stater cubicle will NEVER be smaller than a DOL cubicle.


"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln  
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies  

RE: IEC Soft Starters

Another general answer - if you find a soft-starter that isn't much bigger than a DOL starter, the load on the motor better be easy to start and you need to pay attention to the current and number of start per hour you attempt.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources