check valve on Rupture disk outlet

check valve on Rupture disk outlet

check valve on Rupture disk outlet

(OP)
There is a need of providing the flow switch at outlet of Rupture disk installation for liquid relief application to tank. 65 psig back pressure is created because of flow of liquid in another pipe where the RD will be discharging, which is 2000 ft long line going to tank.
Instrument asked me to provide a check valve at outlet so that when there is flow in otherline where RD outlet is connected the flow switch does not sense the flow.
My question is "can I provide a check valve at Rupture disk outlet?"

RE: check valve on Rupture disk outlet

You already have such a mess that you can pretty much do anything you want.  I'm going to assume that you've done all the pressure drop calculations and with 2,000 ft of pipe you still have adequate flow, that you have taken into account the possibility of phase change and possible cavitation, that if the second stream is variable your rupture disk will still handle the capacity required.

With all that, a check valve will add a psi or so of extra backpressure as long as it doesn't scale up and seal itself closed.  I wouldn't put a check valve in a safety device discharge, but then I also wouldn't dump it into a process line or run it 2,000 ft.  

Flare headers are used all the time and are occasionally longer than your 2,000 ft, but I've never heard of comingling safety-device exhaust with a normal process, but maybe that is just that I've never heard of it.

David

RE: check valve on Rupture disk outlet

I would say no.
Any restriction in a pressure relief path should not be installed.
Orifice plates, in-line flow meters (switches), check valves are at the top of my list of restrictions.
You can detect rupture disk activation by other means.  

RE: check valve on Rupture disk outlet

Like a BDI - burst disk indicator.  Google it.

Good luck,
Latexman

RE: check valve on Rupture disk outlet

What's the set pressure of the application?  Do the pressures work out so you can put a RD at the application and another at the outlet such that the 65 psig backpressure will not burst the one at the outlet?  Just wondering.

Good luck,
Latexman

RE: check valve on Rupture disk outlet

Maybe you should look at a buckling pin system.

Regards
StoneCold

RE: check valve on Rupture disk outlet

Downstream of pressure relief device, devices potentially causing partial or total blockage which further limit the relief flow shall be avoided. Check valve is one of the potential device.

Burst disk indicator (proposed by Latexman) and buckling pin system with positional switch (proposed by StoneCold) are good idea in detecting RD opening. Besides, provision of double RD with pressure transmitter is another way.

If you select flow switch as mean to detect opening of RD, make sure it does not form a device potential causing partial blockage of relief flow path.

 

 

JoeWong
Chemical & Process Technology

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources