Story drift!

Story drift!

Story drift!

(OP)
I am designing steel moment frames for a steel building - one story. What is the story drift limitation per AISC for steel buildings? I heard it is H/400, however, I could not find this requirement in AISC. I would appreciate help.

RE: Story drift!

It depends on the cladding.  For brick, H/400 is reasonable if you use the 50 year wind.  
Check out AISC Design Guide #3 - Serviceability Design Considerations for Steel Buildings

RE: Story drift!

(OP)
StructuralEIT,

Per AISC, 13ed, section L4 (pp. 16.1-144), it reads as .................... shall not exceed the limiting values of such drifts that may be specified by the applicable BLDG code. Do you know if IBC has this limitation specified? If yes, which section?

RE: Story drift!

IMHO Drift design is not particular well codified unless you're talking about seismic.  

One reference that I have gives the following design recommendations based on what type of exterior cladding or interior partions you have:

Exterior cladding:
Brick veneer or unreinforced concrete = L/400 to L/600

Tilt-up concr = L/200

Plaster / Stucco = L/400

Architectural Precast concrete, stone clad = L/400


Interior Partitions:
Drywall / plaster = L/400

Unreinforced masonry = L/667

Reinforced Masonry = L/400

Tile, Hollow clay brick = L/2000

Brick = L/1250

Also, your elevator may require drift control as well.  To me this would be based on input from the mechanical guys.  But, the design guide recommends L/400.  



 

RE: Story drift!

(OP)
Thanks JoshPlum.

RE: Story drift!

Josh,
I would be interested in looking at your reference book.

RE: Story drift!

Wind drift limits are not codified - they are up to the judgment of the engineer.  The limits presented in Design Guide 3 as recommended above are fairly typical.   

RE: Story drift!

A nice reference is

Serviceability Limit States Under Wind Load
Lawrence G. Griffis
National Steel Construction Conference 1994 Proceedings
AISC

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources