NEC ?'s - 110.14(C), tables 310.16 & 310.17, 392, 400
NEC ?'s - 110.14(C), tables 310.16 & 310.17, 392, 400
(OP)
We are using #4/0 AWG dual rated "type-W/RHH" flexible power cable on a job. The manufacturer's data sheet lists the cable as rated 405A @ 90C based on NEC table 400.5. We will be terminating the cable to a power terminal block rated 75C. The cable is going to be installed in an uncovered cable tray in a single row, no spacing between cables. No temperature deration is required - it's a temporary 3-week job and it is cold outside.
Based on the RHH rating:
The conductor is rated 405A per table 310.17 90C column. Must be multiplied by 0.65 per article 392.11. New rating is 263.25A @ 90C. Per article 110.14(C), the cable ampacity must not exceed 230A per table 310.16 based on 75C column. The lower of the two values is 230A, so that must be my cable ampacity. Correct?
Based on the type-W rating:
If I had the cables in "free air" run on the ground and spaced appropriately, the ampacity of the cables @ 90C would be 405A. If I were using camlock connectors on both ends (rated 405A @ 90C), the entire cable could be rated 405A, right? If I take that same cable and terminate to that terminal block or to a breaker, would I then have to use 230A ampacity per article 110.14(C)?
Another question:
What is the purpose of article 392.11(B)(3) if article 110.14(C) forces you to limit the ampacity of the 75C column of 310.16?
Based on the RHH rating:
The conductor is rated 405A per table 310.17 90C column. Must be multiplied by 0.65 per article 392.11. New rating is 263.25A @ 90C. Per article 110.14(C), the cable ampacity must not exceed 230A per table 310.16 based on 75C column. The lower of the two values is 230A, so that must be my cable ampacity. Correct?
Based on the type-W rating:
If I had the cables in "free air" run on the ground and spaced appropriately, the ampacity of the cables @ 90C would be 405A. If I were using camlock connectors on both ends (rated 405A @ 90C), the entire cable could be rated 405A, right? If I take that same cable and terminate to that terminal block or to a breaker, would I then have to use 230A ampacity per article 110.14(C)?
Another question:
What is the purpose of article 392.11(B)(3) if article 110.14(C) forces you to limit the ampacity of the 75C column of 310.16?






RE: NEC ?'s - 110.14(C), tables 310.16 & 310.17, 392, 400
If the cable tray ran along a boiler where ambient temperature was 55C, we could start the derating from the 90C columsn. The final ampacity of the complete cable, breaker, & termination system would be the least rated element. In many cases that is the 75 C termination.
RE: NEC ?'s - 110.14(C), tables 310.16 & 310.17, 392, 400
Article 392.11(B)(3) allows you to use the ampacity given in 310.16 without further de-rating. Normally, cable in tray must be de-rated below ampacity in 310.16 unless conditions in 392.11(B) are met.
David Castor
www.cvoes.com
RE: NEC ?'s - 110.14(C), tables 310.16 & 310.17, 392, 400
Best to start with the 75 deg number and work down from there if you need to.
Alan
RE: NEC ?'s - 110.14(C), tables 310.16 & 310.17, 392, 400
Thank you for your help!
RE: NEC ?'s - 110.14(C), tables 310.16 & 310.17, 392, 400
This is true only if the conditions are the same along the whole length of a circuit. The 75C limitation of the connectors at the breaker, fuse or MCC is the maximum circuit ampacity, but the rest of the circuit may have a higher rating.
For example: a 250 kcmil circuit starts at an MCC in an air-conditioned room, ambient 30C, runs underground in a duct bank then overhead with conductors spaced one diameter apart in a tray on a pipe rack with process piping at 60C, then down to the equipment in a conduit with 3 other circuit carrying conductors in a 40C ambient.
At the MCC, the 75C rating column is applicable with no derating for temperature. (255A).
For the underground, we can use the 90C rating as the starting point for the underground duct bank ampacity calculations. (290A x derating factor from Ampcalc calculations= ??)
Conductors in the tray have to be derated for the high ambient temperature conditions, but again the starting point can be the 90C ampacity for conductors in free air. (455 A x .71= 323A)
The wires in the final run of conduit carrying 6 current carrying conductors has to be derated 80% plus derated for 40C ambient (91%). (290 x 91% x 80% = 211 amps).
The wires are good for 211 amps in this circuit, (assuming the UG duct bank calc's work out). If we had started with the 75C rating for all of the derating calc's ampacity would be 186 amps.
RE: NEC ?'s - 110.14(C), tables 310.16 & 310.17, 392, 400
Alan
RE: NEC ?'s - 110.14(C), tables 310.16 & 310.17, 392, 400
Is there some sort of official document by NFPA or other group that explains these sizing requirements (especially the termination requirements of 110.14(C)) in detail and gives examples like you have given?
Our business group is going to have a hard time with this, so it would be nice to have something from an official electrical safety group. The mentality is "we've been using this cable for 405A service for 20 years, there's no way it can be rated 202.4A." (this is where a panelboard or breaker or similar device has terminations rated 75C installed in an area of 40C ambient temperature)