Motor conductor minimum size

Motor conductor minimum size

Motor conductor minimum size

(OP)
I have an existing 500hp motor drivin through a VFD.  There are parallel 500MCM cables.  There is also a bypass contactor around the VFD.  We plan to upgrade to 600HP motor.  I can limit the output of the drive to 600HP.  If I use the FLA of the new motor 680 x 1.25 then I need a cable good for 850 amps.  I am feeding the drive and by-pass contactor from a LVCB with an 800Amp trip unit set at 800Amps.  I know that the 125% sizing is based on service factor and power factor,etc. Does the NEC allow me to use smaller than a 125% sized conductor if my overcurrent protection is set below that?

RE: Motor conductor minimum size

No.

David Castor
www.cvoes.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources