deadman anchorage
deadman anchorage
Some deadman anchorages are being designed. Are there any typical depth for the anchorage and what do you recommend(minimum) for depth of site investigation for the location of the deadman concrete elements.In a similar project in silty fine sand materials they advised 13' long x 2' deep x 3' wide concrete deadman buried 6' in the ground.
Am looking for a design manual that explains the typical values and how to calculate/estimate the pull-out load.
What is the recommended depth of site investigation for the above case history. I guess about 10'. Your advise would be appreciated.
RE: deadman anchorage
Attached is a US Army Corps of Engineers Design Manual for Sheet Pile Walls. It gives a procedure for designing a deadman anchor (Chapter 5, page 5-10). Make sure the deadman is behind the passive wedge of the wall!
Unless you have a geotech report, you will be relegated to the allowable passive pressures of the IBC.
Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask