Once you have calculated the total inbreathing and outbreathing of the tank how do you then determine what size vent you should use if you are using a open swan neck breather.
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Tank Venting
This can be software or a manual method such as the Crane Technical Bulletin.
The swan crane vent is modeled as pipe. First assume a pipe size.
The model has 1)entrance loss, 2) length of pipe for nozzle, 3) 180 deg return bend 4)exit loss.
The entire model should handle the vent flow and have friction loss less than relieving pressure.
If not, increase the pipe diameter.
The method works for both pressure and vacuum.
If there is a bug screen on the exit, some additional safety factor should be added -- could be one pipe diameter larger.
RE: Tank Venting
API-650 requires venting per API-2000. And API-2000 requires that vents be flow-tested. So technically, you can't meet the requirement just by calculating flow rates without flow-testing (except for lifting-cover roof manways, that is.)
The ASHRAE handbooks also have flow information for various fittings (including screens) that can be applied to tank vents.