Hello friends, I am supervising the construction of an API 650 tank farm. Our contractor has installed electrical ducts around the tank bases at about 12" from the walls, I didn´t find it in the code, but we never saw them installed this way, any experience on it?





RE: Ducts around API tanks
RE: Ducts around API tanks
RE: Ducts around API tanks
Please see the picture attached on the right on top of the concrete ring you can see the electrical conduits.
RE: Ducts around API tanks
RE: Ducts around API tanks
Generally these are instrumentation and lighting - low voltage and amperage. It is common to locate these as shown in your pictures.