Fabricator substituting standard holes with short-slotted

Fabricator substituting standard holes with short-slotted

Fabricator substituting standard holes with short-slotted

(OP)
Fabricator is asking for short-slotted holes where we spec'd standard holes.  Steel member is a "typical" simple-span W-shaped beam with only gravity loads. Fabricator shows slots perpendicular to load (horizontal) as we'd like to see them.  Connection is pretty standard stuff (from my vantage point) - designed as bearing with high strength bolts, threads included, finger-tight.  

From a design/calc standpoint, are there any checks necessary to approve the short-slotted holes?   My quick once-over of the code makes me think the fabricator's recommendation is OK.  I'd like to approve the change as I know the short-slotted holes will help the erectors with fit-up.


Apologies as the Q may seem trite or simple but I'm an EIT with 2+ years of concrete design practice experience doing shops on my first steel design - just trying to save myself a bit of code-hunting.  

2nd Q: Any other general shop drawing/CA/field inspection tips for a steel newbie?

RE: Fabricator substituting standard holes with short-slotted

Just make sure he uses plate washers instead of the standard washers.  OK from there.

RE: Fabricator substituting standard holes with short-slotted

What's the reason for finger tight?
To me that implies you are expecting some horizontal movement within the joint, and therefore slotted holes would be expected.

RE: Fabricator substituting standard holes with short-slotted

(OP)
Forgive me, snug-tightened bolts are what we truly spec'd and is reflected as such on the shops.  Freudian slip above (I've been trying to self-educate on the AISC bolt spec and other steel lit quite a bit recently).

The short-slotted holes are necessary from the erector's perspective because we have a few bays of supported slab being expanded into a confined, existing space.  Apparently all the long-slotted holes we included didn't keep them happy enough.

RE: Fabricator substituting standard holes with short-slotted

Plate washers are not required for short slots.  

What is the connection material?  Single plate (shear tab) connections?  

AISC 13th Ed allows for single plates with up to 3 1/2" eccentricity, with no consideration of eccentricity on the bolts (straight shear).  SEE 13th ED p10-101

This applies to a single column of bolts only.  For multiple columns eccentricity must be considered.  And slip-critical bolts must be used with short slots.

This also assumes that the connection is not to a concrete embed.  Single plates are "rigid" connection, therefore the embed must consider the moment, rather than shear only.  

RE: Fabricator substituting standard holes with short-slotted

connectegr...agree plate washers not req'd. for short slots...many fabricators long slot the holes anyway when short slots intended.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources