tower load combination

tower load combination

tower load combination

(OP)
This is my first time to design 230kV transmission tower and 60m tall communication tower. I dont know the load combinations to be used both for these towers. Do they have the same resistance factors also?

RE: tower load combination

Check your code requirements.  I'm not sure what those are in your location.

RE: tower load combination

If you are designing within the United States.

Communication towers are usually designed to one of the TIA codes (F or G).  

Transmission towers are governed by some other code.  I'm not familar with it, but I think it's ASCE-10.   

RE: tower load combination

Where I am the utility has there their own spec/code stipulating loads and combinations.
There are also industry body codes with loading recommendations/requirements.

RE: tower load combination

(OP)
k, tnx guys. I'll try to do some research

RE: tower load combination

You will need to use the NESC - National electrical safety code.  It has guidance on Transmission Towers.  for Communication towers you will need to use TIA-EIA-222-G.

RE: tower load combination

Pat76, FYI there is a forumn for Communication Engineering and Transmission Structure Engineering. In the USA, mike07civil is correct regarding the NESC (which is a code adopted by most states) and the TIA-222-G (which is a standard adopted by many companies and some jurisdictions).

For these two documents, the load factors, resistance factors, load cases and limit states are very different.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources