220 from 240/480
220 from 240/480
220 from 240/480
how do I get 220 from a bank of 240/480 tramsformers?
RE: 220 from 240/480
220 volts is a standard utilization voltage in the USA.  The corresponding delivery voltage is 240 volts.  The difference allows for voltage drop in the LV distribution system.  220 volt equipment will work with a 240 volt supply.
Two ways:-
1. Reduce the voltage you are feeding them with.
2. Change the turns ratio.
You will need to give more specifics to get a half decent answer.
Marmite
check closer. Any equipment rated for 220 Volts may also be rated for 50 Hz.
220 Volts was a standard voltage in North America once but was uprated to 240 Volts about 50 years ago.
Why do you think you need 220 Volts?
Bill
"Why not the best?"
Jimmy Carter
You need to provide more details.
Whatever is rated for 220V should be fine operating at 240V.
If the transformers are configured as 3-phase then you have 480V/277V.
The other common 3-phase connection is 208V/120V.
240V/120V is the common 1-phase house or small building feed.
We have no idea what power configuration you actually want.
Another configuration is the 240:480 delta. Many 240 Volt transformers will drop to 228 Volts on the minus 5% tap. What is your application? How many KVA do you need? Is this a school question? (trick question?)
Look at an auto-transformer or Variac.
Bill
"Why not the best?"
Jimmy Carter