220 from 240/480
220 from 240/480
(OP)
how do I get 220 from a bank of 240/480 tramsformers?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: 220 from 240/480
RE: 220 from 240/480
1. Reduce the voltage you are feeding them with.
2. Change the turns ratio.
You will need to give more specifics to get a half decent answer.
Regards
Marmite
RE: 220 from 240/480
220 Volts was a standard voltage in North America once but was uprated to 240 Volts about 50 years ago.
Why do you think you need 220 Volts?
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: 220 from 240/480
Whatever is rated for 220V should be fine operating at 240V.
If the transformers are configured as 3-phase then you have 480V/277V.
The other common 3-phase connection is 208V/120V.
240V/120V is the common 1-phase house or small building feed.
We have no idea what power configuration you actually want.
RE: 220 from 240/480
Look at an auto-transformer or Variac.