Open Delta Connection - part 2
Open Delta Connection - part 2
(OP)
I have encountered an open delta 3-phase 240V service in PA and have been confused by so many different explanations. I understand the B (high or stinger leg) is at 208V to ground. Can a single pole breaker then be used (if connected to the B phase bus) to power a 208V piece of equipment?






RE: Open Delta Connection - part 2
Sure, it might work for a while, but it will be no end of trouble and confusion for anybody who has to work on the system, and it loads up both transformers.
RE: Open Delta Connection - part 2
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Open Delta Connection - part 2
For this application, you would need a single-pole MCCB rated at 208- or 240 volts, and not 120 or 120/240 volts.