Low resistance measuring - High vs. Low current methods
I have to buy some micro-ohmmeter for field testing of contact resistance of CB's, disconnector switches, busbar joints, etc.
I have a choice between instruments using high DC current and low DC current. Both types have sufficient resolution and accuracy, that with low DC (actually 2A)can be used also for measuring of transformer windings resistance.
Could you advice me whether there are some advantages/disadvantages of both methods, as well as some specific standard requirements? I work in the IEC world, but suggestions based on ANSI requirements are also welcome.
It may be like this in theory and practice, but in real life it is completely different.
The favourite sentence of my army sergeant
RE: Low resistance measuring - High vs. Low current methods
Then, I would look for an 'anti-thermal EMF' feature. Sometimes, the thermo-EMF influences super low ohms readings and it may be necessary to do two measurements with reversed polarities to compensate for that.
Using high current makes the thermo-EMF problem less pronounced, but the equipment is heavier and I do not see any reason to use high current.
So, low current, four wire and (perhaps) a possibility to compensate for thermal EMF is what I would look for. Plus storage and print-out possibilities.
Gunnar Englund
www.gke.org
My big concern with using a high-current test set on a transformer is that it needs to be gently ramped up in current and back down otherwise there can be a huge inductive voltage produced when the test leads are disconnected.
My only concern was if any standard requires using of high currents, as most of traditional instruments on the market are that type. But I suppose it is mostly because technology that allow to produce precise low current microohmeters have not been available before.
ScottyUK before to find that low current instrument I also considered T&R instrument. I am quite happy from their primary injection test sets. But to add one more heavy box for transportation ...
I have seen 'low ohm' tests carried out with ordinary ohm-meters with tens or hundreds of milliohms in test leads.
One recent case was the mapping of bonding resistance over a 100x200 m2 area. Two wire ohm-meter was used and resistance measured never below .4 ohms. It happened in an industrialized country...
Gunnar Englund
www.gke.org
I had an HP6681A supply with a precision shunt and a couple of good bench multimeters - a Keithley 2000 and an Agilent 34401A - and managed to get results better than 1% accuracy at 10nΩ. The thermal emf problems Skogs mentioned are very evident when the volt-drop you're measuring is a few microvolts, and it helps if the meter has an averaging function.
To summarize what I heard (and agree with):
[*]4-lead measurement – most important
[*]Thermal EMF's tend to become important at low measurement levels.
[*]Manual or built-in-auto reversing of polarity compensates for most interfering noises such as thermal EMF.
[*]High current requires slow rampdown to avoid voltage transient... also sometimes slow rampup due to test equipment limitations.
I would add one item:
High current creates higher voltage drop and tends to create higher signal to noise ratio against for all possible sources of noise. Auto reversing of measurement polarity may not provide perfect cancelation and output stability depending on variability and frequency of the interfering noise. This becomes a more important consideration when interfering quantities become very large compared to measured quantities as might be the case in field measurement of low resistance using low current. I think some of the low current devices will be more sophisticated than others in terms of method used for identifying and cancelling interference (megger mentions a "point / slope method").
Now a question. I have noticed as zogzog said there is a tendency to specify/require the higher current measurement such as 10A or 100A when referrring to contact resistance measurements. I don't know why that is (any suggestions?). I don't think there are typically any non-linear effects even at contact surfaces (do others agree?). I think maybe it is just that contact resistances tend to be very low when measuring directly accross contact (compared to for example winding resistances) and the specifier is making some assumptions about the ability of test equipment to provide required accuracy/stability/repeatability in presence of noisy environment. (?).
Should've been:
[*]High current for inductive winding resistance measurements requires slow rampdown to avoid voltage transient... also sometimes slow rampup due to test equipment limitations.
I am still curious why.
The only time when higher voltage and higher current is definitely a necessity is when semi-conductive materials like carbon are in the circuit because they exhibit very non-linear behaviour at low voltages.
I have not seen a specification requiring a 100A low resistance tester in many years. My idea is that this requirement was based on the fact that in the past the measuring part of the instrument (including the dial type meter) did not have good accuracy at low voltage and that the high current was required to produce the higher voltage necessary for a good reading.
I employed it many times very successfully to measure transformer winding resistances & busbar connections.
The make was Megger.
We can all make guesses, but an instrument which is perfectly adequate for testing distribution bus joints and breakers might be useless on a generator circuit breaker or main bus. For example, the joints at an 18kA generator main bus wouldn't even register on a Ductor, and if it did then the reading would be meaningless. I've tried; why do you think we had the huge 500A power supply and lab meters?
So for those applications there is need for instruments that work on very low measurement current. But that reduces the magnitude of measured voltage which requires more sensitive and precise voltage measurements which drives cost and complexity (and imo noise susceptibility) up.
In the power equipment world, we have large conductors with higher heat capacities and more surface area for heat dissipation and self heating would usually not be a concern at levels like 10A. I think that is why we can often get a cheaper alternative that accomplishes what we want using higher signal levels and less sensitive measurement electronics.
Please find attached catalogue sheet for the instrument I have in mind. Texts are in Bulgarian language, but data in the table are clear enough (I have translated texts there). I am considering type M2420A, another type has same ranges, but with higher accuracy, which is not necessary for me.
According to me this instrument should be OK for my needs. My only concern was about standard requirements for measurement current. As I understand from the discussion, most probably there is no such standard defined, so 2 A current is looking OK.
By the way, I asked a colleague from independent calibration laboratory for his experience with the instrument. He stated that they have calibrated several of these in last years without any problems in the accuracy and stability. So I am going to invest in one. But your opinions will be highly appreciated too.
linky
http://www.motwane.com/MWRM4.htm
What do you guys think ?
Muthu
www.edison.co.in
IEC 60694 Common specifications for high-voltage
switchgear and controlgear standards
6.4 Measurement of the resistance of circuits
6.4.1 Main circuit
The current during the test shall have any convenient value between 50 A and the rated normal current.
This result doesn't make me happy ...
The paradox - we have to try to read the mind of the standards-writers. Are they requiring 50A because:
1 – Historical. In the old days there was not a reasonable available low current device to make those measurements accurately in the field. So they assume lower current measurement won't be as accurate and specify higher current measurement .(in which case it would have made a lot more sense to just specify an accuracy rather than a test current).
....or...
2 – they know something we don't?
My problem is that I am in procedure for accreditation of Inspectuion Body in the company. These people from accreditation agency are looking only in the papers and will not accept any deviation from the standard even if the instrument injects 49,9 A instead of 50.
They rejected my test forms because resistance units are written as Ohms, instead of the corresponding Greece letter !