relief valve
relief valve
(OP)
Is necessary to install the relief valve after the volumetric pump?
I've the max punp discharge at 4.2 bar g and the design pressu re of pipe is 10 barg. Is it possible that the pressure arrive at the pressure design
I've the max punp discharge at 4.2 bar g and the design pressu re of pipe is 10 barg. Is it possible that the pressure arrive at the pressure design





RE: relief valve
However, the valve could also be for minimum flow...
Best regards
Morten
RE: relief valve
RE: relief valve
If so (i.e. pump curve quasi-vertical), then safety valve should be installed at the pump discharge.
This is because in case of blocked outlet scenario (no flow = no frictionnal pressure drop), the pump developped pressure will increase until it overcomes the pressure drop for which it has been designed. Indeed, this type of pump is not dead-headed like a centrifugal pump.
I propose:
- Set pressure = 10 barg
- Relieving floware can be assumed equal to the rated flowrate of the pump.