Modulating Pilot - when to use

Modulating Pilot - when to use

Modulating Pilot - when to use

(OP)
Under what circumstances should I consider a modulating, vs. non-modulating, pilot valve?

RE: Modulating Pilot - when to use

My understanding is that modulating valves can be used to avoid PSV chatter due to oversizing.  In one case, a client of mine bought a vessel with a large orifice (16 sq inch) relief valve.  The vessel needed only a 4 sq in orifice and I determined the cost of switching to a modulating pilot was actually less than the cost of purchasing a more moderately-sized relief valve.

One case where a modulating would not be recommended is if you have a high Joule-Thompson effect during discharge.  In some cases, ice could potentially form (if discharging vaporizing water) and block the discharge.

There are certainly other reasons to choose one over the other too but those are my thoughts.

RE: Modulating Pilot - when to use

As another consideration, typically you will not want a pop open pilot valve for liquid relief scenarios in order to avoid liquid, hydraulic hammer issues.  You should consider the modulating design for liquid relief.

Here are some additional considerations...
http://farris.cwfc.com/Products/spokes/reliefValves.htm

RE: Modulating Pilot - when to use

One of the main reasons in choosing valve action type is, modulating will keep constant discharge, pop (or sometimes known as "snap acting") give fast relief & reseating pressure well below set pressure.
If your system is constantly working over set pressure, a pop acting will keep blowing off, reseating, blowing off, reseating.....a modulating valve will keep constant discharge..(think of it a a pressure regulator action....working on discharge)...I would get my knuckless whacked by my old chargehand should he read this last bit.
Ciao,

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources