Hydropheumatic tank sizing

Hydropheumatic tank sizing

Hydropheumatic tank sizing

(OP)
NC admin code give an example of sizing a hydro tank as peak demand - pumping capacity x 20 min = required effective volume
so if i have (60-30)x20=600 gallons
then they state the total volume if you use a 60-40psi pressure cycle with automatic air water volume controls is required effective volume/0.25. So 2400 gallons
I assume this is based on Boyle's Law.  What affect and how do you calculate the volume with precharging? How does this work. With no control the percentage of water would be 7% of the total volume on a 60-40 pressure cycle. so 8570 gallons in my example. Big difference. School me please.

RE: Hydropheumatic tank sizing

(OP)
Very usefull, thanks for the information.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources