VFD Power Modeling

VFD Power Modeling

VFD Power Modeling

(OP)
Team,
I'm trying to develop a mathematical relatiionship for the HP(or KW)for a Motor controled by a VFD. The motor is a 1150 HP 600VAC, 40 HZ 6 pole motor. I have a theoretical model showing a linear relationship from 0hz to 40hz. HP is constant to a point after that, I know. I'll have different motors later. The idea is to control the amount of KW used for power management (below rated HZ). Basically, I will be given a KW limit and will have to determine the speed necessary to reduce the motors KW to at, or just below this limit. Using the theoretical model, I can use the equation for a line, but was looking for a mathematical formula, such that I can just switch motors and get the data for the new motor (i.e. switching from 1150hp to 1500hp).

RE: VFD Power Modeling

The horsepower is determined by the load, not the motor.

RE: VFD Power Modeling

wzrdstrm,

Compositepro is right.  For example, if your load is a pump in a variable-flow system, horsepower at a given speed will depend on the position of the control valves (i.e., how much flow is being demanded).

Rather than trying to model the drive/motor/pump system, which can be extremely complex and subject to lots of measurement error, why not just put a PID controller or PLC in with a watt transducer as input?  That could be arranged to control the VFD to maintain whatever upper limit you have set at the time.

All this assumes you have a load that can be safely starved of power, of course...  Fans, pumps, etc..., in HVAC systems that aren't critical might be adaptable -- what's your motor doing, anyway?  If it were a sewage pump, it could get really messy...

Good on ya,

Goober Dave

RE: VFD Power Modeling

Recheck if your VFD has the PID function or if you can control it by a torque adjusment fucntion inside. Other option is that you can use the the analog output signal configured as a Power or energy signals and with a small PID controller feedbak the analog VFD's speed input

Fernandoelec

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources