Steam Rates For Low Pressure Flares
I'm after a guideline on the ratio of steam to flare gas required for smokeless operation of a low pressure continuous flare.
Steam Rates For Low Pressure FlaresSteam Rates For Low Pressure Flares(OP)
Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesWhat is rapid injection molding? For engineers working with tight product design timelines, rapid injection molding can be a critical tool for prototyping and testing functional models. Download Now
The world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
RE: Steam Rates For Low Pressure Flares
Bset Regards
Morten
I believe the steam rates vary from about .1 lb steam/lb HC up to about nearly 1:1 ratio depending on the gas in question. Some HCs burn essentially smokeless (methane) while olefins and other unsaturates can be very difficult to burn smokeless (but can be).
In general the steam works in three different ways.
Primarily it cools down the core of the flame so that the "cracking" reaction is suppressed and delayed and the carbon doesn't form until the outer edges of the flame so that it can't grow to unburnable proportions.
Then there's the mechanical mixing and turbulence which it introduces into the gas/steam/air mixture which helps to promote more rapid conversion by bring the oxygen into more intimate contact with the "cracking" gas.
Finally, there is some benefit from the addition of the OH- radical into the mix which sweeps up some C+ into -CHO which is a gaseous radical rather then the C-C-C-C which is a solid.
Having said all this the range of requirements starts at roughly 0.2 w/wt for light paraffinic materials, into 0.35 - 0.45 for refinery type mixtures and developing beyond 0.6 wt/wt for aromatic and olefinic mixtures. These latter gases all have heats of formation which are intrinsically positive and therefore do not benefit from the cooling as much as the aliphatics.
Another factor is the flare tip diameter because it influences the flame diameter and the dwell time until the gas meets the air. Bigger flare tips use more steam than smaller tips for the same gas.
Hope this helps you.
If you're really stuck let me know.