Combined Neutrals
Combined Neutrals
Combined Neutrals
Here's an oddity I came across.  An electrician was called to a house, because of lights flickering.  He came to believe there was an open in the neutral of a 2-wire branch circuit. But he was unable to locate and correct the open.  So, he jumpered the neutral to the neutral of another 2-wire branch circuit, in an existing outlet box.
Which sections of the NEC did he violate?
Another question, please.  Why is this forum titled "IEEE (electrical) Code Issues Forum"? Wouldn't "NEC (electrical) Code Issues Forum" be more appropriate?
RE: Combined Neutrals
300.3(B) would be one issue.
NEC is only for US, this is an international forum.
resqcapt19:  Thanks - I agree that 300.3(B) would be a great reference for this.
BtW - I've visited several forum sites lately.  For most of them it's readily apparent where to find the best forum for NEC topics/questions; but not for this one.  It seems that there should be a separate forum titled "NEC Code Issues Forum".
NEC is part of (or recognized by) ANSI/IEEE codes and standards. There are two distinct worlds out there, IEC and ANSI/IEEE for electrical codes/standards.
IEEE seems is very appropriate as this is an international forum, as EEJamie stated.
Rafiq Bulsara
http://www.srengineersct.com
And yet you found it looking around  It seems to work out OK since we have an IEC forum and NEC questions pretty clearly don't belong there.
(I suppose NEC questions could be posted in the NFPA forum, since the NEC is NFPA 70, and has always been primarily a fire prevention standard.)
David Castor
www.cvoes.com
I did find it - but only through some persistence. I've used the NEC for nearly 30 years, and have been an IEEE member for nearly 20, but I don't typically associate one with the other. For the places I've worked (e.g., A&E design firms & petro-chem), the term "IEEE" is rarely used, except pertaining to standards & reference materials.
But the term "NEC" is used much more frequently, especially when a discussion of Code comes up.
I'm just thinking from a keyword/marketing point-of-view; something that catches the eye quicker, for NEC-related topics.
BtW - DPC, how did you insert the "Quote"?  I see no option for that (I'm using FireFox).
Put the text to be quoted between
Quote:
David Castor
www.cvoes.com
[quote] text to be inserted [/quote/
When the last slash / is changed to a square bracket ] you will get the quote box.
Quote:
text to be inserted
You may also use:
[quote Dave] text to be inserted [/quote/
Quote (Dave):
text to be inserted
Bill
"Why not the best?"
Jimmy Carter
rwilsond:
You can see all TGML codes by clicking on "Process TGML" link below the answer box. Also make sure that that box is checked.
Rafiq Bulsara