RURAL WATERLINE

RURAL WATERLINE

RURAL WATERLINE

(OP)
thread164-244163: Not meeting minimum fire flows

IT WAS REFERENCED IN THE PREVIOUS THREAD, IF U CAN'T OBTAIN FIRE FLOW, THEY INSTALLED A DRY HYDRANT WITH AN UNDERGROUND STORAGE TANK.  I'M THINKING THIS WOULD BE A PRACTICAL WAY TO GO.  CAN ANYONE POINT ME IN THAT DIRECTION FOR INFORMATION ON THE MINIMUM SIZE OF THIS TANK, CAD DETAILS, COST COMPARISON?  

AS MENTIONED YESTERDAY I HAVE STATIC PRESSURE OF 130 RESIDUAL PRESSURE OF 88 AND A FLOW RATE OF 100 GPM.  IT CURRENTLY HAS A 2" LINE BORED UNDER A HIGHWAY AND I HAVE A PROPOSED THREE INCH LINE RUNNING 800 FEET TO A DEAD END LINE WHERE I'M WANTING TO INSTALL A DRY HYDRANT. I HAVE NEVER WORKED WITH DRY HYDRANTS BEFORE THOUGH    

RE: RURAL WATERLINE

Are you required to provide fire flows in a rural areas? If so, what state/country are you working in? Rural water lines that I have designed had to be able to flush at 2.5 ft/s and maintain at least 20 psi throughout the system and  every meter must have 30 psi.     

RE: RURAL WATERLINE

(OP)
RURAL, GOSHEN ARKANSAS  ITS WITHIN THE CITY LIMITS AND CALLED A SUBDIVISION, SO YES IN THIS CASE THE CITY ORDINACE SAYS I NEED TO PROVIDE A FIRE FLOW, OR I MAY BE ABLE TO INSTALL A DRY HYDRANT, AND GET MY WATER TO THE PROPOSED TANK THROUGH MY PROPOSED 3" SERVICE LINE THAT WOULD FILL THE TANK AND KEEP IT FULL.  JUST NEVER DONE THIS BEFORE.

RE: RURAL WATERLINE

Here is an example of a "dry hydrant".

http://www.dof.virginia.gov/fire/dry-hydrants.shtml

http://www.ettfire.com/underground_tanks.html

http://www.dryhydrants.com/news&info.htm

ftp://ftp-fc.sc.egov.usda.gov/NHQ/practice-standards/standards/432.pdf
"Water Requirement. The quantity to be
considered available to a dry hydrant is the
minimum available (at not over 15 feet total
static lift) during a drought. A minimum of
30,000 gallons (1.1 acre-inches) of pumpable
impoundment water or a minimum pump flow
rate of 250 gpm without interruption for 2 hours
is considered a dependable water supply."

RE: RURAL WATERLINE

Sounds like very small pipes, very high velocity, and also with very high pumping head loss if must fire flow 250 or more? gpm  (equivalent to 360,000 or more gpd).  For such very high velocity, hope pipes are pretty strong, too!

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources