Smart questions
Smart answers
Smart people
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

LINK TO THIS FORUM!

Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

Partner With Us!

"Best Of Breed" Forums Add Stickiness To Your Site
Partner Button
(Download This Button Today!)

Feedback

"...Over the past year I have found your site to be EXCELLENT. Never have I been able to find so many answers to such vast problems and it is an excellent service..."

Geography

Where in the world do Eng-Tips members come from?
buddy91082 (Electrical)
23 Feb 10 10:18
Looking to calculate voltage drop on a 12kV ciruit that is a few miles long. Is the voltage drop formula for medium voltage the same as low voltage. Anyone know of a link to an online voltage drop calculator?

Thanks.
b
rbulsara (Electrical)
23 Feb 10 10:28
The Ohm's law, V=IZ is the formula, which remains the same. You need to get the right impedance (X and R) data.  Use per phase values.

Just be careful as to what formula you use, as some 'customized' formula would ignore reactance for smaller size wires at low voltages and you cannot ignore that at higher voltages.

You may want to visit some MV cable manufacturer's website such as okonite.com to get some assistance and data.

As for the link, your web search would be as efficient as mine.

Rafiq Bulsara
http://www.srengineersct.com

jghrist (Electrical)
23 Feb 10 10:57
for balanced loads, the voltage drop formula is the same:

VD = I·(R·cosø + X·sinø) where power factor = cosø

If your phases are not balanced, things get more complicated.  You can account for the imbalance by using a sequence phase impedance model as described in "Distribution Feeder Line Models" by W.H. Kersting of New Mexico State University.  This model correctly accounts for the effect of unbalanced loading and mutual coupling for fully transposed lines using standard equations for sequence impedances.
 

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close