Motor Differential CTs
I need to spec differential CTs for a 3400kW Induction motor. I wish to use 3CTs instead of 6 (by running the phase and neutral through one CT. The FLC is 204A. The CT supplier is asking for a detailed spec before they make the CTs to order. They need knee point voltage as well as volts per turn. Accuracy class is ClassX - or the equivalant. The fault level is 8kA for 3ph and 3kA for 1ph fault.
Kevin Bosch
Rainbow Technologies
RE: Motor Differential CTs
Kevin Bosch
So much easier to call out the desired C rating and not worry about all those other parameters that go along with the rating; I'd say that even a C200 would generally do quite well in that application (I don't know that relay though).
If you want the diferential protection, the best is the use of 6 CTs
Fernandoelec
How can you get the differential current?
Muthu
www.edison.co.in
I hear it called "core balance", and I find it to be VERY common here on the US Gulf Coast. You do need to specify a six-lead motor, so that you have access to both the line and neutral ends of each winding. As David said, both ends of a phase's winding go through a single CT.
You can see an example in the manual for the GE Multilin's SR469 manual under "differential current inputs". There's a picture, too.
Another cool part of the concept is that you don't have to worry about two CT's having different saturation characteristics.
old field guy
Muthu
www.edison.co.in
And yet this is seems to be the best method. Wish I had thought of this idea. :)
Muthu
www.edison.co.in