Hope you guys can help me on this
Hope you guys can help me on this
(OP)
Hey guys,
I'm wondering if anyone can refer me to the correct ways of dP cell transmitter(daiaphragm seal) CALIBRATION. vented tank . (filled gycerine) can anyone come up with a better method for this calibration?).
and i'm new in this field....
Hope you guys can help me on this. Thank you in advance.
I'm wondering if anyone can refer me to the correct ways of dP cell transmitter(daiaphragm seal) CALIBRATION. vented tank . (filled gycerine) can anyone come up with a better method for this calibration?).
and i'm new in this field....
Hope you guys can help me on this. Thank you in advance.





RE: Hope you guys can help me on this
RE: Hope you guys can help me on this
Are you attempting to establish/configure a range for transmitter by doing a wet calibration?
Is the transmitter HART compatible? Do you have a HART handheld?
Is the diaphragm seal close coupled to the transmitter or on capillary?
RE: Hope you guys can help me on this
yes m wanna do wet calibration.
yes d transmitter was hart compitible and we have 1..
d transmitter was endress hauser pmd 78 wit diaphragm seal..
and its cappilary type...
tq 4 ur reply bro
RE: Hope you guys can help me on this
You empty the tank, do "set LRV"
You fill the tank to your known upper level, and do "set URV".
You need to know what that physical height distance is between lower LRV and the URV because that's what the 4-20mA output will span. Whatever you send the 4-20 to needs to know what the 20mA represents (assuming your 4ma is zero)
I can't say it any better than E&H does:
RE: Hope you guys can help me on this
one more thing m want to know ...before tis d measuring mode they set to "level" and unit set to mmh20...can u explain to me bout mmh20..bro
is it correct measuring mode set to "level" and "mmh20"..?
Hope you can help me on this. Thank you in advance.
RE: Hope you guys can help me on this
Are you familiar with this unit of measure?
If not, pick another unit of measure (in the US we use inches) . . .
Whether it is millimeters or inches, it is still height/length/distance.
The measurement made is at the density of water, so you'll have to correct the length/distance value by the specific gravity of glycerine.
indicated height / SG = actual height
indicated height is what comes out of the transmitter
RE: Hope you guys can help me on this
i got it ...tq 4 ur help dawn...actualy last time m work as a smt engineer at sony ericson{electronic company) now m work at petrochemical company and work as electrical & instrument engineer...m only has experince in radar level transmitter{yokogawa}m expert in troubleshooting pcb ...control card...inverter repairing...etc
nice to meet u ...later if i have any problem i'll getch u k...
have a nice day bro...tq tq tq
RE: Hope you guys can help me on this
I am glad you found the help you required. For future reference, Eng-Tips Forums are Modern English speaking forums. Most of us do not speak or prefer not to interpret hieroglyphics, Sanskrit, Mayan, Aramaic, Latin, Greek, Anglo-Saxon, tweet speak, text speak, or any other kind of symbol syntax. Please do your best to utilize proper Modern English including grammar and punctuation when posting.
Thanks.
RE: Hope you guys can help me on this
We are not impressed with ur tx. And we do not feel like we want to help someone that doesn't think we deserve decent language.
Try better next time!
Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
RE: Hope you guys can help me on this