Soil resistivity for a 138kV substation

Soil resistivity for a 138kV substation

(OP)
Hello all,

What kind of soil resistivity test is used to obtain soil resistivity values to be used to design a ground grid for a 138kV substation? I see the 4 point wenner method is used and also lab resistivity testing with the soil sample.
Which method is generally used by utilities or others for substation ground grid design.
Also, there's a peaking power plant about 100ft away with a different owner and the ground grids will NOT be tied together. Will this affect the results of any of the soil resistivity tests?
Thanks in Advance!

RE: Soil resistivity for a 138kV substation

The 4 point Wenner method is the most commonly used resistivity test.  I gives values of resistivity at different depths, which is important for ground grid design.  A lab resistivity test only gives the resistivity for the sample taken.

Resistivity at large depths is required for large grids.  Measuring the resistivity at large depths requires large probe spacings, and the grid 100 ft may affect the results.

See 81-1983
IEEE Guide for Measuring Earth Resistivity, Ground Impedance, and Earth Surface Potentials of a Ground System.
 

RE: Soil resistivity for a 138kV substation

(OP)
jghrist thanks for your comment. I'll look this up.

RE: Soil resistivity for a 138kV substation

There are several acceptable methods to test the soil resistivity.  The 4 points Wenner method is one of them.

Most meters today have filters to isolate electrical noise.

The effect of an energized facility 1000' apart may not introduce significant distortion in the test.

Soil resistivity measured in the lab from sample, many time are not representative of field conditions.

Regardless the method used to test the soil resistivity, the measured apparent resistivity require interpretation to obtain a equivalent soil model (uniform or multiple layers) by the Sunde's method, least square, etc.

See the enclosed link for additional reference.

http://www.lyncole.com/pdf/Lyncole_Ground_Test_Methods.pdf

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources