Heat Generation
2

Heat Generation

Heat Generation

(OP)
Hi,
I am looking to determine the size of my air-conditioning unit and I am missing two pieces of information. Can someone provide me with the heat generation (Btu/hr or kW) for a typical computer as well as a computer screen?
I have my HVAC textbook at home so I do not have access to the information.
Thank you in advance.
Gabriel

RE: Heat Generation

I think plug load is easy, just use one of those watt-meters. ASHRAE has standard numbers. It really depends on the office, there also are copiers, printers etc.

I think all the other information is harder to get (infiltration, ventilation, perimeter walls and roofs, solar gain through glazing, humans).

If nothing else, an office PC with LCD screen should not be more than 100W. Obvioulsy you can have dual grafics card and play videogames and 400 W are possible, obviously I want to work in that office  smile

RE: Heat Generation

ASHRAE 2001 Fundamentals - 29.12 Table 8
Average Heat Gain from Computer Eq:

Computers ( Continuous / Energy Saver Mode)
Avg (55w/20w)
Conservative (65w/25w)
Highly Conser (75w/30w)

Monitors (Continuous Only)
13-15in - 55W
16-18in - 70W
19-20in - 80W

Hope that helps.
D

 

 

RE: Heat Generation

It looks like the monitor numbers are for CRT monitors, LCD are significantly lower. On the other hand there is a trend to dual-monitors.
If you have proper CAD work stations I'd say 100W for the PC.  

RE: Heat Generation

(OP)
AggieDave, that was exactly what I was looking for. Thank you very much! I will use the conservative approach for now because it is only a ballpark value we are looking for to size an air-conditioning unit.

Thanks!!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources