3-Winding Transformer Equivalent Model
2

3-Winding Transformer Equivalent Model

3-Winding Transformer Equivalent Model

(OP)
Hi everyone,

I'm confused about how to model a 3-winding transformer as three 2-winding transformers in star-formation. I was under the impression that it is a simple Delta-to-Star conversion of the impedances, but it is not according to some.

I've got an Autotransformer with a delta tertiary winding 330/132/22kV, 490MVA with the following impedances based on its rate:

Zps = 0.2081 pu
Zpt = 1.0045 pu
Zst = 0.7530 pu

If I follow a conventional Delta-to-Star transformation, then:
Zp=(Zps*Zpt)/(Zps+Zpt+Zst) = 0.10635 pu
Zs=(Zps*Zst)/(Zps+Zpt+Zst) = 0.01967 pu
Zt=(Zpt*Zst)/(Zps+Zpt+Zst) = 0.38481 pu

However, according to a different formula it should be:
Zp = (Zps + Zpt -Zst) / 2 =  0.2298 pu
Zs = (Zps + Zst -Zpt) / 2 = -0.0217 pu
Zt = (Zpt + Zst -Zps) / 2 =  0.7747 pu

Which of these calculations is right and on what bases?!
Thanks in advance for your help.

-Radi
 

RE: 3-Winding Transformer Equivalent Model

The second formula is the correct one. You can refer it to the references like Protective Relaying Principles & Relaying by Blackburn or Elements of Power System Analysis by Stevenson.

regards,

RE: 3-Winding Transformer Equivalent Model

(OP)
Ok... I can see that almost everyone saying that it is the second formula. My problem is to do with the resistance.
I can still accept a negative reactance (as shown above), but will also yeild negative resistance, which is hard to accept!

Thanks

RE: 3-Winding Transformer Equivalent Model

The negative impedance is a mathmatical construct the has no physical meaning. The star point of the three impedances has no physical meaning, but simply exists to make the math work. It is only terminal-to-terminal that has physical meaning and all those impedances work out correctly.  

RE: 3-Winding Transformer Equivalent Model

ahmedradi,Transformer engineers were getting baffled by these negative reactances and resistances during the first half of last centuary.Then the GE veteran, A.Boyajian removed the mystery by his classic AIEE 1933 paper" Progress in Three Circuit Theory"You can read a summary in Chapter 4 of Blume's famous  book "Transformer engineering" where  the meaning of negative  reactance and resistance are explained.

In factory we find out the resistance value of each circuit by measuring losses by pair and applying formula similar to the one you mentioned for impedances to arrive at losses of each circuit.From that R is calculated out. Then from measured impedance of each circuit, reactances are calculated.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources