Air Core Current Limitimg Reactor
Air Core Current Limitimg Reactor
(OP)
The reactor is 12.9 kV; 600 amp; (13.4 MVA) X=5% I would like to obtain a typical X/R ratio, but could not find an answer anywhere. Could someone please help me.
Thank You
Thank You






RE: Air Core Current Limitimg Reactor
In the IEEE standard C57.16 - 1996 Paragraph 10.2.2 it states that the standard multiplier K is 2.55. If you now look at the chart you will see that this value requires an R/X ratio of .07. of course this value will vary between manufacturers however if you are looking for a typical number this should suffice.
Note: This makes the X/R = 1/.07 = 14.28
RE: Air Core Current Limitimg Reactor
Jack