Applicability of Simplified Wind Method.
Hi all,
IBC (03) 1609.1.1 says that wind loads shall be determined per ASCE 7 (02) with one of the exceptions being "Wind loads determined by the provisions of Section 1609.6," which is the simplified method. Section 1609.6.1.2 gives conditions under which the simplified method can be used for components and cladding. Well, ASCE 7 (02) Section 6.4.1.2 gives 5 conditions, all of which must be met in order to use the simplified method for components and cladding. All of these conditions can be found somewhere in the IBC except the last one which states, "the building is not subject to the topographic effects of Section 6.5.7 (i.e., Kzt = 1.0)."
It seems that the ASCE 7 is adding an additional requirement on top of the IBC. Is this correct? In my region, a location where Kzt = 1.0 is non-existent. Does that mean I can never use the simplified method? No one in my office ever noticed this before because if you can use the simplified method per the IBC, one would never bother to pick up the ASCE 7 in the first place!
Thanks in advance for your comments.
RE: Applicability of Simplified Wind Method.
It is OK for simple projects, but for the more complicated and larger projects, use EFM.
Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
Mike McCann
MMC Engineering
Motto: KISS
I have mostly used the simplified method for wind and the equivalent force method for siesmic.
Garth Dreger PE
AZ Phoenix area
The IBC 06 refers to the ASCE 7-05 only for determining wind loads. For the simplified method, the ASCE 7-05 does not have the condition that Kzt=1.0.
So in my opinion you are OK with using the simplified method.