Does anyone know a good reference for determining the usable life of an electromechinical relay?

I know we have had to replace some capacitors, but other than ocasusinal failures they seem to be holding up well.

RE: Life of an Electromechinical relay

They were so well designed, I don't think we know what their useful life is yet.  Most of the problems I see are the bearings wearing and causing timing and/or reset issues with the disc.

I am speaking of the IAC and CO units.

Probably see more problems with the older ACR and RC reclosing relays.

Alan

RE: Life of an Electromechinical relay

I've seen some that have been in service since the 50's...  They will likely be replaced before they ever fail.  Refular maintenance on these relays is necessary though.

RE: Life of an Electromechinical relay

It's going to depend on what type of relay is under consideration and the service.   

David Castor
www.cvoes.com

RE: Life of an Electromechinical relay

I used to regularly test some GE and Westinghouse protective relays that were in service continuously since the 1940's.  After sixty years of service they were still hitting the original curves and functioned perfectly with only an occasional cleaning and I never had to worry about software and firmware upgrades.

Of course when one caught a fault and operated, all it did was drop a little orange flag.

old field guy

RE: Life of an Electromechinical relay

The orange flag hadn't faded yet?  That is a high quality relay!  

RE: Life of an Electromechinical relay

oldfieldguy Did you still keep also the original laptop which have been used for their initial programming winky smile

By the way, I often say that the biggest mistake of relay engineers was when we left design of relay protections to computer guys. The result is 500+ pages User Manual for overcurrent relay !
smile

------------------------
It may be like this in theory and practice, but in real life it is completely different.
The favourite sentence of my army sergeant
 

RE: Life of an Electromechinical relay

(OP)
We have someone trying to justify replacing the IAC relays because they are old. So the question needed to be asked.

My coworkers said, 75 years or the span of two protection engineers.

I do believe that in this case the panels included ACR's, which seem morl likely to become jammed due to lack of grease, or hardining of the orignal grease (we'll blame it on poor maintenance).


 

RE: Life of an Electromechinical relay

You can always replace the ACR with something like the BE1-79A that is a work alike replacement solid state relay without having to replace the IACs.  What every you eventually replace the IACs with won't last as long and won't do time overcurrent any better.  What the replacement will do much better is a bunch of stuff the IAC can't do - reclose in the same relay - and even better the replacement will provide a whole lot more information about what did, and more importantly didn't, happen for any given event.

RE: Life of an Electromechinical relay

YEP....Have used the Basler as an ACR replacement on many occasions.

Alan

RE: Life of an Electromechinical relay

(OP)
Once upon a time I used a Basler ACR retrofit, and I had problems with it.
First problem was the ACR case wasen't wired as expected. That corrected, the next time it was called on to reclose, it was burned up.

The replacment we purchased was better to work with.
 
However they haven't reported any problems yet.
I just don't want to go replacing relays because they are old. I want to see a real reason.

Thanks for your input. This is good information

RE: Life of an Electromechinical relay

The "old" electromechanical relays did and still do a great job for what they were designed to do....and like was said, I have not upgraded the firmware in one yet either!

Granted there have been many instances where I have needed different curves or functions and could have used a micro based relay, but most of the time they are perfect for the job.

The manufacturers are always pressing to get the latest and greatest set of bugs (firmware upgrades) in all of the existing relays in the field, but I do not do the upgrades unless absolutely necessary.  I have upgraded the firmware in relays and had them not operate as advertised.  Then I end up flashing it back to the old version.  That means that every time I do the upgrade, I am also doing another full commission test....and who needs to be doing that!

The capability of a few cycle delay in the inst is what I miss most of the time.

Alan

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources