What went wrong?
What went wrong?
I work for an electric utility company and am trying to figure out what went wrong in the scenario below:
A new commercial building was in the middle of construction and we were called out to energize the brand new transformer we had installed to serve only this building. Upon energizing the transformer, a resident drove up and reported smoke in their hourse. A few minutes later, the fire department showed up and stated they were getting reports of smoke in several homes on the street and told us to shut off power to the transformer. Further investigation showed some burn damage on a water pipe about five feet from the transformer. The theory is an electrical ground fault travelled on the water pip and entered several homes nearby and damaged some of their appliances and electronic equipment. We checked the transformer and the primary connections and nothing was wrong. My question is, what could the electrician have done wrong on the secondary of the transformer that could have caused this event? The electrician ran the secondary cable from the transformer, to the new commercial building, and terminated the wires at the meter at the building and the secondary of the transformer (we witnessed the secondary terminations).
The electrician had not bonded to the water pipe in the building yet, so if the phase and neutral cable were switched, the main water pipe which it is believed carried the fault, could not have been energized.
RE: What went wrong?
Keith Cress
This seems odd. Most inspectors won't approve an installation for service until the grounding system (electrodes, conductors, bonding, etc.) is in place. What is your utilities and the inspection authorities process for verifying completed inspections and approvals and energizing new services?
Is it a pole-mount or padmount transformer? Did any overcurrent device trip?
Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.
Bill
"Why not the best?"
Jimmy Carter