Table 1604.5 2006 IBC vs. Table 1.1 ASCE 7-05
Table 1604.5 2006 IBC vs. Table 1.1 ASCE 7-05
(OP)
2006 IBC table 1604.5 notes "any other occupancy with an occupant load greater than 5,000" is an occupant category III. Table 1.1 in ASCE 7-05 does not have this requirement. Per section 102.4, it appears the 2006 IBC will control. Has anyone else sought clriafication for this from ASCE or ICC? Are they going to clean up this discrepancy in ASCE 7-10?






RE: Table 1604.5 2006 IBC vs. Table 1.1 ASCE 7-05
RE: Table 1604.5 2006 IBC vs. Table 1.1 ASCE 7-05
Also, in the IBC table, whether you excceed 300, or 5000, you are still in Category III.
RE: Table 1604.5 2006 IBC vs. Table 1.1 ASCE 7-05
RE: Table 1604.5 2006 IBC vs. Table 1.1 ASCE 7-05
Check your state and local code amendments to the IBC.