no rise analysis flood zone fema
never done one... a "no rise analsyis"
would it be worth the learning curve?... must back test with fema data and then model the moved and changed drainage channel the client made without permits to prove that there is no rise in the flood levels upstream (downstream?)... HecRas or other program I suppose. How long does one of these take? i know it would depend on size of area, quality of data, etc... but, any input is helpful. How happy will the client be when we say it will cost... ????
RE: no rise analysis flood zone fema
1. You are running a backwater elevation analysis and making sure that the backwater elevations do not change due to any construction.
2. Also, the downstream elevations cannot not increase due to additional outflow capacity from construction.
In either event, flooding would occur as a direct result of your project, which is a no no.
As to the cost, could be very minimal for small projects, or extensive with larger projects interrupting a large percentage of the floodplain. The one I did was very small and able to be verbally justified without calculations.
Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
"would it be worth the learning curve?" It really depends upon your level of comfort with H&H projects. HEC-RAS will probably be the model you use. If there is an existing HEC-RAS model, you'll save a little time.
The first thing I like to do is speak with the local floodplain administrator - if they participate in the NFIP and they have FEMA floodplains then they have to have a floodplain administrator.
As for time, 2-3 months. Cost - most are not cheap but the cost does vary with complexity. There is a considerable amount of liability involved with these projects.
If the channel has been moved, FEMA will require a LOMR within 6 months of project completion.
Robert Billings
www.newrivereng.com
and as far as removing their development, in fact i have consulted with several firms, and the cost would likely be around 4-6k+... or more! (depnding on the quality of fema data, surveying requirements, etc.) so, im not sure about the removing the development being less than the study argument. it seems to me that a statement of engineering judgement (and its subsequent liability if incorrect) should be enough on a project of this scale... maybe 400 feet of channel in question (for example.. the channel has not been moved signifantly - maybe 50 feet, and has been widened, the excavated soil from the channdel removed from the flood plain, the downstream culvert is undersized according to the community master plan so therefore there is an argument that it will not affect downstream levels, and by similar argument of channel capacity and its"retention/detention" vs its original capacity, neitgher will it affect the upstream...) will try this approach, although when the community developers get an idea that something is requried, they wont accept anything but... a quick scan of the fema requirements states that an explanation of why a no rise analysis isnt required may be accepted in lieu of the actual model results... ofcourse, the actual hydrology is more complicated, but are the models really that precise when we are talkin about a project of this scale, and when the data to begin with is less than desirable?
If you are in a FEMA regulated floodway and you have moved the creek, you are required to submit technical data showing that you have not increased the water surface elevations (CFR 60.3)or you must apply for a CLOMR. If you are doing construction in a FEMA floodway (CFR 60.3(d)), you are required to have a floodland development permit, and either a "no-rise" or a CLOMR.
Please be careful. I'm not trying to be Chicken Little screaming the sky is falling, but I know engineers that did not take the FEMA rules seriously and ended up in front of the Board. I've also been involved in a major lawsuit involving FEMA floodway issues. The lawsuit went all the way to the NC superior court. So, I'm suggesting you do some major CYA on this one.
"it seems to me that a statement of engineering judgment (and its subsequent liability if incorrect) should be enough on a project of this scale" This is not correct. Based on what I've said before, a letter stating that based on engineering judgment the project will not increase WSEs will not be sufficient.
Robert Billings
www.newrivereng.com
"but are the models really that precise when we are talkin about a project of this scale"
No they are not. As engineers we know how many assumptions are made with the CNs, Manning's values, Tc's, etc. Does it matter that the models are not that precise - No. FEMA has estabilished a standard for a "No-Rise" study to be less than 0.00 feet. This is not defined in the CFR but is defined in the MT-2 forms and more recent FEMA correspondence. FEMA world does not always match up with reality.
Robert Billings
www.newrivereng.com
FEMA has become more aggressive over the last 10 years. Whenever you need to work near a FEMA area, talk to the local FPA and/or the State NFIP coordinator.
Robert Billings
www.newrivereng.com