Does anyone have any experience in installing HV (400 and 132 kV) surge arresters upside down, hanging on a metal gantry 20m above the ground?
I've seen this type of arrangement due to lack of space around a transformer. Are there any (electrical) disadvantages that may arise from this?
I am assuming from civil viewpoint it's not a good thing to hang heavy porcelain surge arrester.
 

May you grow up to be righteous, may you grow up to be true...

RE: HV Surge arresters

Assuming your support is built for the weight, I don't see why weight would be an issue. Generally the sheds are shaped for the orientation, so you might want to order the arresters custom for this application. While you're at it, consider polymer over porcelain. Much lighter and easier to install. And when they fail, they won't take out bystanders and transformer bushings.

RE: HV Surge arresters

No electrical issues if proper clearances are maintained.  You should verify with arrester supplier that they are suitable for inverted mounting.   

David Castor
www.cvoes.com

RE: HV Surge arresters

(OP)
Are you sure that length and any 90 degrees angles of the link to the ground won't affect the proper functioning?

May you grow up to be righteous, may you grow up to be true...

RE: HV Surge arresters

Lead length always affects performance, and shorter is better. Measure it from the protected insulation, round trip. In this case it is the sum of the length from the transformer bushing to arrester plus the ground lead from arrester to transformer tank. I'm not aware of any issues with 90s.

RE: HV Surge arresters

We no longer mount arrestors upside down as a precaution.  

We had a 115 kV arrestor mounted upside down that failed, although we could not conclusively identify the cause.  The best guess at the time was that the attached bus work did not have enough thermal expansion joints which caused some deflection of the arrestor which combined with the upside down orientation to allow water ingress.  

RE: HV Surge arresters

Sometimes they fail inexplicably even when mounted right side up.  looking around

David Castor
www.cvoes.com

RE: HV Surge arresters

Excessive side loading in any orientation is a bad idea.  

RE: HV Surge arresters

But if the design did not allow for thermal expansion of the bus, the arrestor would have probably still failed if upright at some point.  Many units are mounted inverted and do not have problems if they are designed for it.

Alan

RE: HV Surge arresters

It very well could have been a random failure, but changing to more standard orientation was quite easy to do.

The side loading was not excessive, however it was cyclic which led to a theory that it had been flexed back and forth enough to allow water ingress.    

Glad to hear others have had good experiences with upside down mounting.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources