I might be asking a silly question,

We have a transformer, which is fed from 4160V systrem. On the primary, we have fuse and relay to provide Short circuit and overload protection respectively. On the secondary, we have a circuit breaker(600V) to provide short circuit and overload protection. However, the primary relay is not large enough and overload trip will occur. I am thinking of disabling it since downstream Circuit breaker can provide Overload protection as well, also this is only short period of service, which is about 15mininutes. Any comments would be appreciated.    

RE: Overload Protection for Transformers

In principle it sounds OK to me. It would be unusual in any case to trip the primary circuit breaker for an overload on the LV side that can be cleared by tripping the LV circuit breaker. Are you sure that the primary side relay is providing overload protection though? What are the curve and settings?
Regards
Marmite

RE: Overload Protection for Transformers

(OP)
Yes, Marmite,
Both primary and secondary sides are providing O/L protection. We set primary settings higher than secondary settings.  

RE: Overload Protection for Transformers

If this installation is governed by the National Electrical Code you should take a look at Article 450. Primary fuses must not exceed 300% of full load current.

Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.

RE: Overload Protection for Transformers

You must have short circuit protection on the primary of a transformer. Overload protection may be applied on the secondary side only.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Overload Protection for Transformers

Hi.
Not needed.
Maybe.. possible only connect PT100 on the transformer ( if is dry) to some monitoring, like to DGPT.

Best Regards.
Slava

RE: Overload Protection for Transformers

It would work.  It could be justified as a temporary fix to get around an equipment failure while you wait for replacement parts, etc.  That's a compromise to be made  "in the heat of battle", so to speak.

I would not choose it for a permanent installation.

In the terms of cost, if you're already forking out money for a 4160 volt installation, the added cost a of a dedicated control power transformer (CPT) is relatively small.

If you're modifying aging equipment to upgrade protection and control, it makes no sense to add several bad failure modes by using a PT to do the CPT's job.

System protection is not well served by compromises of this depth.  Most of us in system protection tend to be conservative because most of us are still remembering horror stories that start with "that should be good enough" and "I never expected THAT to happen."

old field guy

RE: Overload Protection for Transformers

The fuse and relay on the secondary do not protect for a transformer internal fault.
 

RE: Overload Protection for Transformers

Hamid:
By CEC rule #26-252(4) and Table 50 you can use fuses up to 200% of the transformers FLC if the transformer impedance is between 7.5% and 10%.
If the transformer is less than 7.5% impedance you may fuse the primary at 300%.
This is contingent on proper overload protection on the secondary side.
Again from Table 50, For a breaker that is not more than 250% of the rated current of the transformer.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Overload Protection for Transformers

(OP)
Thank you guys for all the inputs. It is justified to diable this  primary overload protection as a temperary means. But we will have to have the primary O/L protection since the primary fuse rating is higher than 200% FLA.   

RE: Overload Protection for Transformers

Hamid:
If you want a definite answer, you must tell us:
A> KVA?
B> Wet or dry?
C> Setting of secondary breaker?
D> % Impedance?

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Overload Protection for Transformers

... and what codes apply here.

Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources