Minor Losses - Internal Pipe Stiffener

Minor Losses - Internal Pipe Stiffener

Minor Losses - Internal Pipe Stiffener

(OP)
Need k value for connecting HDPE to PVC with an internal pipe stiffener and mj restraint system (FM project) to calculate minor losses.  We are thinking of assuming reducer and increaser for k value.  Do others typically include this connection in their hydraulics and if so what do they use.  (We will have about 26 sections and with a k value of 1, it adds about 6 feet of head to TDH at the operating point.) No luck with manufacturer that I called or internet search.  Thanks.

RE: Minor Losses - Internal Pipe Stiffener

(OP)
Just received this info/dwg from manufacturer -

The Lengths can be either 10" or 7".  As for the OD/IDs, I'd recommend the items below for the Pipe ID you've given.  The Stiffeners are made with a lead-in taper.  This would be the Min ID of the Stiffener and is only the last inch of the Stiffener.  This dimension is not controlled so only an Estimate can be provided.  

Pipe - 18" HDPE      
ID Size - 15.741
Stiffener OD - 15.585
Stiffener Wall Thickness -.25
Stiffener Min ID (Est.) - 14.75

Pipe - 18" C905
ID Size - 17.180
Stiffener OD - 17.00
Stiffener Wall Thickness - .25  
Stiffener Min ID (Est.) - 16.25
 

RE: Minor Losses - Internal Pipe Stiffener

K value of 1 is a reasonable assumption. I would not normally include something as minor as this. This amount of head loss is much less than the margin of error for your system calculations.

RE: Minor Losses - Internal Pipe Stiffener

(OP)
Thanks bimr.  I appreciate your remarks.

RE: Minor Losses - Internal Pipe Stiffener

Whether or not such devices and minor losses at obviously many locations would cause problems probably depends on a whole lot of factors, including the tolerance amount for head loss in the specific application, how realistic pipe roughness for field application one is assuming for the pipe to begin with, is actual or nominal inside diameter being used, and the minor loss calculation and/or confirming test results etc. being employed a the device.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources